If your furnace's air filter is clogged or dirty, it can reduce the amount of air flowing through the system. This lack of airflow will cause your furnace blower to work harder and cycle on and off more often than usual.
There are multiple reasons why your furnace is short cycling. These could include a dirty filter, blocked vent, or malfunctioning flame sensor. You can switch for a clean furnace filter, or have your HVAC technician resolve a more complicated issue.
This may be due to a bad high limit switch or the blower not moving enough air due to blocked vents or weak blower motor due to age.
The top causes to blame when a furnace kicks on and off are: The air filter needs changed. The thermostat batteries need to be replaced. Blower motor malfunctions.
This sounds like a textbook flame sensor problem. Essentially the furnace thinks the flames didn't catch fast enough, and it shuts off the gas valve. It could be that the flame sensor needs cleaning, but sometimes they just need to be replaced.
Insufficient airflow or insufficient gas pressure. A defective, malfunctioning ignition board, flame sensor, light switch, thermostat, thermocouple, fan limiter, or draft inducer fan. The drainage line is blocked, resulting in a full condensate pan. Temperatures are so low that the furnace cannot stay lit.
The simple solution: Turn your furnace off and check the filter. If it's dirty or it's been 3 months or more since you changed it, put a new, high-quality filter in place.
A bad thermostat can be detected when your AC or furnace is not turning on, your HVAC systems are not turning off, the thermostat not responding, your HVAC system is short-cycling, the room temperature not matching the temperature displayed on the thermostat, and the programmed setting resetting themselves.
How Furnaces Normally Cycle. It's actually normal for your furnace to turn on and off throughout the day. Your furnace heats the air in your home and distributes it through ductwork in routine cycles.
The common sources of a furnace clicking sound are:
If it's faulty or dirty, it won't send the signal and the ignitor will click. Ignitor flame — The flame itself can run too cold to burn the gas or oil effectively, so the ignition clicks for several minutes or unendingly.
There is a work-around to waiting. If there is no safety risk (like a gas leak), a furnace can be reset to bypass this wait. Turn off the furnace's power switch and wait 10 seconds before turning it back on.
Check the circuit breaker, thermostat settings, and air filter first as these are common causes of furnace fan failure. Inspect electrical connections, listen for unusual noises, and verify proper airflow through vents during operation.
When a furnace is short cycling, it's working hard to produce heat but isn't making any, causing strain on your furnace. If left unchecked, this could cause major issues for your furnace resulting in hefty repairs.
Turn on the heat on the thermostat and increase the temperature. You should hear a sound from both the thermostat and the furnace, and whichever doesn't make a sound has a problem.
Short cycling indicates a problem within a heater that is cutting off its heating cycle before it finishes. This can be caused by a range of issues, which vary in severity and necessary repair.
Replacing a Thermostat. You'll pay between $15 and $300 for the unit in addition to labor ($65 to $100 per hour) to replace an old thermostat with a new one. However, installing a brand-new thermostat is more involved and, therefore, more expensive.
What Causes Short Cycling? Furnaces have built-in safety systems that prevent dangerous situations like fires, carbon monoxide leaks, or gas leaks. The most likely cause of short cycling is the fan limiter, which prevents fires and furnace damage by shutting the system down if the heat exchanger becomes too hot.
Oversized furnace
This is the most common cause of furnace short cycling. If the furnace has been short-cycling since it was first installed, it may have been improperly sized for your home.
Ask twenty professional HVAC contractors the question, “How Much Does A New Furnace Cost?” and you'll probably get the same answer... “It depends.” On average, the cost of a new furnace can range from $2,000 - $14,2001. However, factors like furnace efficiency, type, size, and much more can impact this range.
If it's broken or malfunctioning, it may fail to detect the flame and shut off the gas supply as a precaution, even if the burners are actually lit. This can result in your furnace starting the ignition process but failing to stay lit.
There are several reasons why your furnace may not turn on. The most common include a broken thermostat, gas line issues, clogged air filters, blocked ductwork, a tripped circuit breaker, and issues with the furnace itself.